The UK Home Automation Archive

Archive Home
Group Home
Search Archive


Advanced Search

The UKHA-ARCHIVE IS CEASING OPERATIONS 31 DEC 2024

Latest message you have seen: RE: Fw: PC Ir receiver that does power on/off


[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: FD10 Filter Question


  • To: ukha_d@xxxxxxx
  • Subject: Re: FD10 Filter Question
  • From: Ian Oliver <ioliver.lists@xxxxxxx>
  • Date: Mon, 13 Aug 2001 10:50:37 +0100
  • Delivered-to: rich@xxxxxxx
  • Delivered-to: mailing list ukha_d@xxxxxxx
  • Mailing-list: list ukha_d@xxxxxxx; contact ukha_d-owner@xxxxxxx
  • Reply-to: ukha_d@xxxxxxx

In article <NBBBLLKOOHNLKHBANMANOELMAOAB.keith@xxxxxxx>,
Keith Doxey
wrote:
> If they are complete Consumer Units with their own main switch and
> Individual MCB's then they can be fed direct from the incoming supply
> provided the tails are of equal or greater rating than the supply
fuse.

But note that there are also discrimination rules to take into account.
It's pretty complex and you need to consider the types of MCBs being used
as well as cable sizes and resistances, but a rough rule of thumb is
never to have a "slave" MCB more than half the rating of a
"master" MCB.
I have a setup like this for a garage CU - the MCB in the main CU is
32A, I have cabled with 10mm cable, the incoming fuse on the garage CU is
60A, and the largest MCB in the garage CU is 16A.

The rule is there so that if there is a fault that the slave MCB trips
and it shouldn't trip to master. This "discrimination" is to
prevent
nuisance tripping of master MCBs that can't be tracked down.

Ian Oliver
Sunny Leeds, UK
Using Java on Tini for control via Dallas 1-wire



For more information: http://www.automatedhome.co.uk
Post message: ukha_d@xxxxxxx
Subscribe:  ukha_d-subscribe@xxxxxxx
Unsubscribe:  ukha_d-unsubscribe@xxxxxxx
List owner:  ukha_d-owner@xxxxxxx

Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/




Home | Main Index | Thread Index

Comments to the Webmaster are always welcomed, please use this contact form . Note that as this site is a mailing list archive, the Webmaster has no control over the contents of the messages. Comments about message content should be directed to the relevant mailing list.